Hi Raul,

 

Please refrain from using the mailing list for direct communications. An update on the Asperitas progress will be included in the next community call.

 

I have responded to you separately.

 

Kind regards,

 

From: OCP-ACS-Immersion-Cooling@OCP-All.groups.io <OCP-ACS-Immersion-Cooling@OCP-All.groups.io> On Behalf Of Raúl Álvarez
Sent: Thursday, 5 August 2021 16:26
To: OCP-ACS-Immersion-Cooling@OCP-All. groups. io <OCP-ACS-Immersion-Cooling@ocp-all.groups.io>
Cc: John Bean <john.bean@...>; eduardo.azevedo@...; don.mitchell@...; Louie Lu <louielu@...>; Steve Helvie <steve.helvie@...>; Daniel Pope <daniel@...>; Peter Cooper <peter@...>; David Montes <david@...>
Subject: Re: [OCP-ACS-Immersion-Cooling] OCP ACS Immersion monthly call (personal invite)

 

Hi Rolf,

 

About the Immersion requirements validation for the Asperitas solution, I'm not sure how's progressing; you mentioned something about a private commitee, which we want to be part of.

 

Best regards,

 

Raúl Álvarez
Lead Solution Architect
+34 637 950 957
Raúl's LinkedIn

 

 

Submer - Datacenters that make sense - https://submer.com
Follow Submer in:
     

 

 

On Mon, 19 Jul 2021 at 23:56, Rolf Brink <rolf.brink@...> wrote:

 

 

Submer Technologies S.L. is a registered company with ID ESB66631375. Data ProtectionYou can enquire what information Submer stores about you and you can request access, rectification, limitation, opposition, portability or cancellation by sending an email to contact@.... Additional information can be found at https://submer.com/privacy-policyConfidentiality: This email and any attached files are intended for the named recipients only and may be confidential. If they have come to you in error, please notify the sender immediately. You should take no action based on them and should not copy or show them to anyone. 


Re: OCP ACS Immersion monthly call (personal invite)

Raúl Álvarez
 

Hi Rolf,

About the Immersion requirements validation for the Asperitas solution, I'm not sure how's progressing; you mentioned something about a private commitee, which we want to be part of.

Best regards,
Raúl Álvarez
Lead Solution Architect
+34 637 950 957
Raúl's LinkedIn
Submer - Datacenters that make sense - https://submer.com
Follow Submer in:
     


On Mon, 19 Jul 2021 at 23:56, Rolf Brink <rolf.brink@...> wrote:


Submer Technologies S.L. is a registered company with ID ESB66631375. Data ProtectionYou can enquire what information Submer stores about you and you can request access, rectification, limitation, opposition, portability or cancellation by sending an email to contact@.... Additional information can be found at https://submer.com/privacy-policyConfidentiality: This email and any attached files are intended for the named recipients only and may be confidential. If they have come to you in error, please notify the sender immediately. You should take no action based on them and should not copy or show them to anyone. 


Re: Reviewing support for "Immersion Requirements rev2"

Rolf Brink
 

--- Please do NOT reply to the mailing list. Instead, address any questions or comments by email to me directly ---

 

Dear members of the OCP ACS and DCF groups,

 

I wish to remind you of the request below regarding “Immersion Requirements revision 2”. The focus group would appreciate your help in the form of content review. You can add your input in the form of comments in the main document or suggest additions in the “Suggested Changes” document.

 

Review document link: https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

Suggested changes document link: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Based on your feedback we are now discussing and adding dielectric fluid quality items to the requirements. Starting August 18, we intend to process all community input, so any comments or additions you may have, will be very welcome.

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

From: ocp-acf@OCP-All.groups.io <ocp-acf@OCP-All.groups.io> On Behalf Of Rolf Brink via groups.io
Sent: Thursday, 22 July 2021 23:36
To: OCP-ACS@OCP-All.groups.io; 'OCP-ACS-Immersion-Cooling@OCP-All. groups. io' <OCP-ACS-Immersion-Cooling@OCP-All.groups.io>; ocp-acf@OCP-All.groups.io; OCP-DCF@OCP-All.groups.io
Subject: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

 

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 


Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

Rolf Brink
 

--moving groups to BCC

 

Thank you, I have added it to the online version of the document and we will discuss it in the workgroup.

 

@All, Please feel free to add more suggestions to the on-line version, as it is editable for anyone on the internet.

 

Please find the link as follows:

https://docs.google.com/document/d/1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0/edit#heading=h.hjd262kbatnv

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

From: ocp-acf@OCP-All.groups.io <ocp-acf@OCP-All.groups.io> On Behalf Of CKC KIMJINBAEK via groups.io
Sent: Friday, 30 July 2021 03:42
To: ocp-acf@ocp-all.groups.io
Cc: OCP-ACS@OCP-All.groups.io; OCP-ACS-Immersion-Cooling@OCP-All. groups. io <OCP-ACS-Immersion-Cooling@ocp-all.groups.io>; OCP-DCF@OCP-All.groups.io
Subject: Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

 


Dear Rolf Brink, Don Mitchell, Mariek and coolant manufacturers,

Thanks for your kind reply and detailed explanation.

 

So,  I added a new suggestion in the attachment.

 

Have a nice summer vacation and keep safe.

 

BR

 



-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor, 20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr

--



 

2021 7 23 () 오후 3:56, Rolf Brink <rolf.brink@...>님이 작성:

Hi JB Kim,

 

Thank you, that’s a great question. To prevent conversations and marketing through the mailing list, I kindly request that you (and all others) include your questions, suggestions and responses in the “suggested changes” document provided. That way, the whole project group will be involved in providing you with an answer.

 

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0.

 

You can also address me directly if you have any inquiries which are related to the work at hand and I will be able to refer you to the specific experts who are involved in the relevant subject matter.

 

I hope this helps.

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

From: ocp-acf@OCP-All.groups.io <ocp-acf@OCP-All.groups.io> On Behalf Of CKC KIMJINBAEK via groups.io
Sent: Friday, 23 July 2021 05:17
To: ocp-acf@ocp-all.groups.io; don.mitchell@...
Cc: OCP-ACS@OCP-All.groups.io; OCP-ACS-Immersion-Cooling@OCP-All. groups. io <OCP-ACS-Immersion-Cooling@ocp-all.groups.io>; OCP-DCF@OCP-All.groups.io
Subject: Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

 

Dear Rolf Brink, Don Mitchell and coolant manufacturers,

 

I want to ask you one question on how to maintain the quality and performance of coolant for a long time. If you already have an answer, I would be very grateful if you could guide me.

In the case of liquid cooling, it is very important to prevent the quality of the coolant from external moisture or contamination. When you talk about the 10-15 year lifespan you are talking about, please give your opinion on how to maintain the quality of coolant.

 

Stay safe and wish all nice summer vacation.

 

Thanks,

JB KIM

 

2021 7 23 () 오전 6:36, Rolf Brink <rolf.brink@...>님이 작성:

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 


 

--

 

-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr


 

--

 

-------------------------------

Kim,Jin-Baek

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr


Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

CKC KIMJINBAEK
 


Dear Rolf Brink, Don Mitchell, Mariek and coolant manufacturers,

Thanks for your kind reply and detailed explanation.

So,  I added a new suggestion in the attachment.

Have a nice summer vacation and keep safe.

BR



-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아(주)

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor, 20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr

--





2021년 7월 23일 (금) 오후 3:56, Rolf Brink <rolf.brink@...>님이 작성:

Hi JB Kim,

 

Thank you, that’s a great question. To prevent conversations and marketing through the mailing list, I kindly request that you (and all others) include your questions, suggestions and responses in the “suggested changes” document provided. That way, the whole project group will be involved in providing you with an answer.

 

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0.

 

You can also address me directly if you have any inquiries which are related to the work at hand and I will be able to refer you to the specific experts who are involved in the relevant subject matter.

 

I hope this helps.

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

From: ocp-acf@OCP-All.groups.io <ocp-acf@OCP-All.groups.io> On Behalf Of CKC KIMJINBAEK via groups.io
Sent: Friday, 23 July 2021 05:17
To: ocp-acf@ocp-all.groups.io; don.mitchell@...
Cc: OCP-ACS@OCP-All.groups.io; OCP-ACS-Immersion-Cooling@OCP-All. groups. io <OCP-ACS-Immersion-Cooling@ocp-all.groups.io>; OCP-DCF@OCP-All.groups.io
Subject: Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

 

Dear Rolf Brink, Don Mitchell and coolant manufacturers,

 

I want to ask you one question on how to maintain the quality and performance of coolant for a long time. If you already have an answer, I would be very grateful if you could guide me.

In the case of liquid cooling, it is very important to prevent the quality of the coolant from external moisture or contamination. When you talk about the 10-15 year lifespan you are talking about, please give your opinion on how to maintain the quality of coolant.

 

Stay safe and wish all nice summer vacation.

 

Thanks,

JB KIM

 

2021 7 23 () 오전 6:36, Rolf Brink <rolf.brink@...>님이 작성:

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 


 

--

 

-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr



--


-------------------------------

Kim,Jin-Baek

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr


Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

CKC KIMJINBAEK <cejnkorea@...>
 

Dear Rolf Brink, Don Mitchell and coolant manufacturers,

I want to ask you one question on how to maintain the quality and performance of coolant for a long time. If you already have an answer, I would be very grateful if you could guide me.

In the case of liquid cooling, it is very important to prevent the quality of the coolant from external moisture or contamination. When you talk about the 10-15 year lifespan you are talking about, please give your opinion on how to maintain the quality of coolant.

Stay safe and wish all nice summer vacation.

Thanks,
JB KIM

2021년 7월 23일 (금) 오전 6:36, Rolf Brink <rolf.brink@...>님이 작성:

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 



--


-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr


Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

 

Hi Raul,
let's keep a conversation free from advertising, brand names - you are doing a great job and with that scarcity of immersion cooling vendors' anybody knows Submer brand already. 

Secondly, I believe JB KIM is not asking "how to prevent water-glycol" from moisture ;) and all understand that immersion systems use hydro carbonated fluids (dielectric oils) and not water-glycol for actual immersion :). 

Anyway JB KIM with the closed immersion enclosures and usual immersion system temperature range + steel tanks -  it is unlikely to get moisture content in the dielectric oil, even in mobile applications without good ambient temp control. Most dielectric fluids are hydrophobic also, so water content is isolated to some extent.
Since insulating oils are used in transformers mostly, there is a lot of expertise in Transformer / insulating oil long-term maintenance. Companies use different oil purification systems from simple multi-filter carts to more sophisticated purification/dehydration / "drying" plants and mobile purifiers/machines. 
Even contaminated dielectric oil, after treatment with vacuum, the multi-stage purifier, will have extremely low water content and will be clean from all impurities. So basically it's about observation, testing of water content (cheap to do on-site or in a remote lab) and if needed - purchase of own filter or ordering quick filtering service from a company dealing with insulation oils. Simple as that, and the immersion system will run for multiple years without any dielectric fluid change.

BR, Maciek
Maciek Szadkowski
CTO at DCX
whatsapp / mobile +48 601 228 528
   m.szadkowski@...   Sales office: Warsaw, Poland  http://cryptocooling.eu/



pt., 23 lip 2021 o 08:44 Raúl Álvarez <raul@...> napisał(a):

Hi Kim,

Raúl Álvarez, Lead Solution architect at Submer. We are an immersion cooling vendor who engineers and produces it's own Technological (Systems and accessories) and chemical (liquid) stack.

Those lifespans are highly dependant on the chemistry of the liquids. Our SmartCoolant liquid, is hydrocarbon-based, which by itself has a minimal amount of moisture, and not water-glycol based. Moreover, we constantly monitor the quality of the fluid with on-board sensors.

Hope I've helped to move you in the right direction.

Best regards,
Raúl Álvarez
Lead Solution Architect
+34 637 950 957
Raúl's LinkedIn
Submer - Datacenters that make sense - https://submer.com
Follow Submer in:
     


On Fri, 23 Jul 2021 at 05:16, CKC KIMJINBAEK <cejnkorea@...> wrote:
Dear Rolf Brink, Don Mitchell and coolant manufacturers,

I want to ask you one question on how to maintain the quality and performance of coolant for a long time. If you already have an answer, I would be very grateful if you could guide me.

In the case of liquid cooling, it is very important to prevent the quality of the coolant from external moisture or contamination. When you talk about the 10-15 year lifespan you are talking about, please give your opinion on how to maintain the quality of coolant.

Stay safe and wish all nice summer vacation.

Thanks,
JB KIM

2021년 7월 23일 (금) 오전 6:36, Rolf Brink <rolf.brink@...>님이 작성:

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 



--


-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr



Submer Technologies S.L. is a registered company with ID ESB66631375. Data ProtectionYou can enquire what information Submer stores about you and you can request access, rectification, limitation, opposition, portability or cancellation by sending an email to contact@.... Additional information can be found at https://submer.com/privacy-policyConfidentiality: This email and any attached files are intended for the named recipients only and may be confidential. If they have come to you in error, please notify the sender immediately. You should take no action based on them and should not copy or show them to anyone. 


Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

Rolf Brink
 

Hi JB Kim,

 

Thank you, that’s a great question. To prevent conversations and marketing through the mailing list, I kindly request that you (and all others) include your questions, suggestions and responses in the “suggested changes” document provided. That way, the whole project group will be involved in providing you with an answer.

 

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0.

 

You can also address me directly if you have any inquiries which are related to the work at hand and I will be able to refer you to the specific experts who are involved in the relevant subject matter.

 

I hope this helps.

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

From: ocp-acf@OCP-All.groups.io <ocp-acf@OCP-All.groups.io> On Behalf Of CKC KIMJINBAEK via groups.io
Sent: Friday, 23 July 2021 05:17
To: ocp-acf@ocp-all.groups.io; don.mitchell@...
Cc: OCP-ACS@OCP-All.groups.io; OCP-ACS-Immersion-Cooling@OCP-All. groups. io <OCP-ACS-Immersion-Cooling@ocp-all.groups.io>; OCP-DCF@OCP-All.groups.io
Subject: Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

 

Dear Rolf Brink, Don Mitchell and coolant manufacturers,

 

I want to ask you one question on how to maintain the quality and performance of coolant for a long time. If you already have an answer, I would be very grateful if you could guide me.

In the case of liquid cooling, it is very important to prevent the quality of the coolant from external moisture or contamination. When you talk about the 10-15 year lifespan you are talking about, please give your opinion on how to maintain the quality of coolant.

 

Stay safe and wish all nice summer vacation.

 

Thanks,

JB KIM

 

2021 7 23 () 오전 6:36, Rolf Brink <rolf.brink@...>님이 작성:

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 


 

--

 

-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr


Re: [ocp-acf] Reviewing support for "Immersion Requirements rev2"

Raúl Álvarez
 

Hi Kim,

Raúl Álvarez, Lead Solution architect at Submer. We are an immersion cooling vendor who engineers and produces it's own Technological (Systems and accessories) and chemical (liquid) stack.

Those lifespans are highly dependant on the chemistry of the liquids. Our SmartCoolant liquid, is hydrocarbon-based, which by itself has a minimal amount of moisture, and not water-glycol based. Moreover, we constantly monitor the quality of the fluid with on-board sensors.

Hope I've helped to move you in the right direction.

Best regards,
Raúl Álvarez
Lead Solution Architect
+34 637 950 957
Raúl's LinkedIn
Submer - Datacenters that make sense - https://submer.com
Follow Submer in:
     


On Fri, 23 Jul 2021 at 05:16, CKC KIMJINBAEK <cejnkorea@...> wrote:
Dear Rolf Brink, Don Mitchell and coolant manufacturers,

I want to ask you one question on how to maintain the quality and performance of coolant for a long time. If you already have an answer, I would be very grateful if you could guide me.

In the case of liquid cooling, it is very important to prevent the quality of the coolant from external moisture or contamination. When you talk about the 10-15 year lifespan you are talking about, please give your opinion on how to maintain the quality of coolant.

Stay safe and wish all nice summer vacation.

Thanks,
JB KIM

2021년 7월 23일 (금) 오전 6:36, Rolf Brink <rolf.brink@...>님이 작성:

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 



--


-------------------------------

Kim,Jin-Baek/Managing director

CEJN Korea Co., Ltd. / 씨이제이엔코리아()

Tel 02-2662-0274~6    FAX 032-232-0637

Room 607, 6th Floor20 Magokjungang 1-ro, Gangseo-gu Seoul, Korea / Zip 07807

www.cejn.kr



Submer Technologies S.L. is a registered company with ID ESB66631375. Data ProtectionYou can enquire what information Submer stores about you and you can request access, rectification, limitation, opposition, portability or cancellation by sending an email to contact@.... Additional information can be found at https://submer.com/privacy-policyConfidentiality: This email and any attached files are intended for the named recipients only and may be confidential. If they have come to you in error, please notify the sender immediately. You should take no action based on them and should not copy or show them to anyone. 


Reviewing support for "Immersion Requirements rev2"

Rolf Brink
 

Dear members of the OCP ACS and DCF groups,

 

I would like to let you know that the new Immersion Requirements Rev2 document has been prepared for broader community review. Since these requirements also relate to facilities and operators, I wish to request review support of both our communities.

 

Document link:

https://docs.google.com/document/d/1VN0yd5bySgiIxwWTpWUcOejionp6cz5D/edit#heading=h.haapch

 

Review scope:

We welcome your support by reviewing the overall content, scope and quality of information.

Please do NOT comment on formatting, grammar or spelling. This will be too difficult to keep track of at this stage.

Please exclude the appendices, as these will be built and completed in the following stages of the document.

 

Special request to ACF group:

I kindly request your attention to chapter 6, “Datacenter Interface Requirements”, as this requires harmonisation with on-going activities.

 

On-going work

The document is still work in progress, so keep in mind that the following is still on-going:

  • Specific content related to fluid references is still being discussed and may be subject to change;
  • All requirements still need to be rewritten and more specifically categorised;
  • Intro and appendices will be finalised at the near-completion stage.

 

Feedback:

Please provide your feedback by means of comments in the document.

Please suggest change proposals or content additions in the following document:

“Suggested changes to ACS Immersion documents”: https://drive.google.com/open?id=1vXaiFskJUy1zsOZZ8OsPFXnQw4xF08ZLYOlRiftcpc0

 

Kind regards,

 

Rolf Brink

Asperitas

Immersed Computing®

 

T: +31 88 96 000 00 | M: +31 6 50 246 338 | E: Rolf.Brink@... | W: www.Asperitas.com

 

 

Find, follow and like us at LinkedIn, Facebook, Google+, Youtube and Twitter!

 

This electronic message contains information from Asperitas, which may be privileged or confidential. The information is intended for use only by the individual(s) or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is strictly prohibited. If you have received this electronic message in error, please notify me by telephone or email (to the number or email address above) immediately.

 

Asperitas | Laarderhoogtweg 18 | 1101 EA Amsterdam | The Netherlands

 


Urgent OCP ACS Vendor Input Request - BIM content of Immersion, ColdPlate, DoorHX, CDU solutions

Don Mitchell <Don.Mitchell@...>
 

Action Request:  Need Revit Content from OCP Vendors For Data Center World

  • If OCP Vendors desire to have their products featured, need ASAP 

 

Immersion, ColdPlate, DoorHX and associated CDU products of keen interest

 

Feel free to attend Weekly OCP ACF workstream update calls Tuesdays 1100 ET (UTC-4) if you wish to discuss

Link for calls listed above https://global.gotomeeting.com/join/952298085

 

 

See Discussion Below and attached PPT

 

Kind Regards

 

Don Mitchell

425-379-8335

Subproject Co-Lead for Advanced Cooling – Facilities (ACF) subproject

OpenCompute.org



Upcoming OCP Advanced Cooling Facilities Events

    • Case Study
    • OCP ACF Workshop on Reference Designs and Connection Standardizations

 

To be added to OCP – ACF Mail group:   https://ocp-all.groups.io/g/ocp-acf

 

 

All,

As an FYI, the BIM request from the ACF group is going to be for file formats such as RFA (Revit). We (MEP consultants) are frequently given SolidWorks, Inventor and other file formats to use which are completely useless to us in our work. Autodesk Revit won’t allow those file types to be directly imported to MEP Design models, so we have to create RFA files. The geometry we get from the aforementioned manufacturer design files are so large that, when RFA files are created from them, they are too large to be used and bring our servers to a standstill. Per Autodesk, RFA files are recommended to be no larger than 500 KB to be useful in Revit models. The one I’m currently working with on a project was 26.5 MB when created from a STEP file.

 

Thank you,

 

John Gross, PE, ATD

Owner, Mechanical Engineer

 

Image removed by sender. __________________________________________________________________

J. M. Gross Engineering, LLC              ENGINEERING

Richmond, TX 77406                           FACILITY ASSESSMENTS

Mobile: (832) 247-6671                     COMMISSIONING

Image removed by sender. __________________________________________________________________

 

From: Caleb Lusk <Lusk.C@...>
Sent: Tuesday, July 13, 2021 2:12 PM
To: Don Mitchell <Don.Mitchell@...>; Michael Schill <michael@...>; rolf.brink@...; jessica.gullbrand@...; Steve MillsOCP <steve.mills@...>; jacob.na@...; bill@...; hamidk@...; michael.berktold@...; michael.berktold@...; jfern@...; Steve Helvie <steve.helvie@...>; rolf.brink@...; sean.t.sivapalan@...
Cc: archna@...; John Gross <john@...>; John.Menoche@...
Subject: RE: R&P - ACS Leads Call - Data Center World Panel Discussion Input Request - BIM content

 

Hi Don,

 

Quick follow up from our PL call. If you wanted to reference the term “Shringwrap” or “Wrap” when referring to suppliers models for BIM use, this is commonly known across Creo (PTC), SolidWorks, and Autodesk (Inventor).

 

Caleb Lusk

Design Engineering Manager

 

Phone: 937.629.2338 • Mobile: 937.869.1271

 

 

From: Don Mitchell <Don.Mitchell@...>
Sent: Tuesday, July 13, 2021 1:14 PM

Subject: RE: R&P - ACS Leads Call - Data Center World Panel Discussion Input Request - BIM content

 

ACS leads – I will be sending out the invite below to many of your members, likely in individual e-mails.  Please advise if you have questions or recommendations on who to target.

Once the concept is demonstrated, believe it will self-justify being a recommendation/requirement.

 

The Advanced Cooling – Facilities (ACF) subproject of OpenComputeProject will be hosting a workshop at Data Center World 16 August

We would like to demonstrate use of BIM/VDC to enable rapid, precision design and delivery of liquid cooled ITE.

 

Need BIM content from ACS Vendors. 

First vendor(s) to provide adequate BIM content as described below will be featured in the discussion and demonstration at Data Center World

Please advise immediately if you have interest in participating.

 

The Reference Design Workstream is due to be published as a WP this summer. 

We are seeking to provide a library of reference designs on liquid cooled ITE. 

(See appendix A or bottom of this e-mail for guidance on BIM Content)

 

 

If you have questions on how to create BIM families in Revit RFA format, we can refer you to contractors that can provide this service quickly.

 

BIM content can greatly enhance the ease of design and delivery of solutions, and advance consideration of ACS solutions.

 

Kind Regards

 

Don Mitchell

John Menoche, P.E.

 

Subproject Co-Leads for Advanced Cooling – Facilities

 

BIM families should have the following characteristics (aligns with LOD 350 definition)

Key Requirements to support Reference Designs

  1. Revit RFA format
  2. Exterior surfaces and clearances with dimensions. 500 KB is the maximum recommended size for RFA files
  3. Connections for piping, power and drain (if applicable) modeled in dimensionally accurate locations and sizes.
    1. Note: if there are straight run requirements for piping connections to facilitate unit-mounted instrumentation, include the straight runs in the RFA so the designer can connect the piping to the RFA and already have straight runs accommodated.
    2. Electrical connections should have voltage, phase, kVA and load classification parameters as a minimum.


OCP ACS Immersion monthly call (personal invite)

Rolf Brink
 


Catch OCP in the new season of DCD>Keeping IT Cool, streaming 14-15 July!

Kate Hendle <kate@...>
 

 
 
Catch OCP in the new season of DCD>Keeping IT Cool, streaming 14-15 July
 
 
We're thrilled to be taking part in the new season of DCD>Keeping IT Cool, a dedicated series focused on the latest research & advancements in IT thermodynamics.

At 3:00pm EDT, 14 July,  OCP Members Robert Lankston, Microsoft; John Fernandes, Facebook; and Kiran Somanchi, CoolIT Systems will preview the different rack-level approaches to air-assisted liquid cooling (AALC) in the episode, "The hyperscale approach to introducing advanced cooling solutions into existing data centers".

Then, at 10:00am EDT, 15 July, we'll take part in another powerhouse episode, "Reusing the heat - what should be done to align current data center business models with future sustainability goals?" with Svein Atle Hagaseth, Green Mountain; Don Mitchell, Open Compute Project; Dr Andy Young, Asperitas; Jaime Comella, Cloud&Heat Technologies; and Vali Sorell, Microsoft.

This expert panel brings together members of the OCP Advanced Cooling Facilities subproject and data center industry to highlight existing applications in data center heat reuse, and the vision of how expanding deployment of liquid cooled ITE can broaden heat reuse opportunities. 

Want to watch? Fill out the short form below & you can stream our free episodes live or on-demand at a time that suits you.
 
 
 
We hope you enjoy!

The Open Compute Project Team
 


Re: Standardizing FWS connections, OCP ACS Immersion Solutions - Thread type, delta T

Dale Sartor
 

Don,

My 2 cents:

I don't think OCP should adopt a global standard for metric threads at the facility level (ACF).  This will not facilitate adoption of liquid cooling in the US where many plumbing components are not widely available in metric.  Every vendor should choose their connections based on their target markets.  Some will have different standards for different markets.

Delta T should not be considered in isolation of supply temperature.  In my opinion it is more important to standardize on design supply temperature, but a combined  supply and delta T standard would be fine.  

Dale

On Tue, Jun 29, 2021 at 4:42 PM Don Mitchell <Don.Mitchell@...> wrote:

The Advanced Cooling – Facilities (ACF) subproject of OpenComputeProject requests your input on standardizing connections to OCP ACS Immersion solutions.

 

Thread connection standardization:   General feedback to date has been:

-          FWS connection point under 2” = metric thread (DN 25 or DN 40)

-          FWS connection point > 2” would grooved coupling connection (or possibly a flanged connection)

Is it better let every vendor choose their thread connection of preference and let the local pipefitter figure it out?

 

Input request:   Do you see benefit to OCP global standard of the connection to the tank options.  (with adaptors used per customer and regional preference)

 

Delta T range standardization: 

  • Diversity in Delta T expectations adds complexity to planning. 

Input Request:  Can the range of delta T options be reduced for OCP solutions.

 

Will be sending a similar survey to ACS Cold Plate and ACS RDHX teams

 

Attached below are workstreams we are seeking to finalize into WPs by end of summer. 

Would value insights on alignment with ACS Immersion guidance

 

 

 

Kind Regards

 

Don Mitchell

John Menoche, P.E.

 

Subproject Co-Leads for Advanced Cooling – Facilities

Progress reviewed

     Weekly OCP ACF calls Tuesdays 1100 ET (UTC-4)

     Weekly OCP Connection subcommittee calls Wednesdays 1100 ET (UTC -4)

     Monthly OCP ACF APAC update 3rd Wednesdays 0930 Singapore/Beiing time – UTC +8)

https://global.gotomeeting.com/join/952298085

 

 

Upcoming OCP Advanced Cooling Facilities Events

 

To be removed from future notices and invites, please respond with request to remove.

 

To get involved: 

1) Please become an OCP member and join the ACF Mailing List  :   https://ocp-all.groups.io/g/ocp-acf

2) Get familiar with the details on the Sub-Project on the ACF Wiki

3) Check our Project Calendar for more info. Call Info and agenda will be published via the mailing list reflector. 

 

To be removed from future notices and invites, please respond with request to remove.

 

 



--
Dale Sartor, PE
Staff Engineer, Building and Industrial Applications
Lawrence Berkeley National Laboratory
One Cyclotron Road, MS 90R3147
Berkeley, CA 94720-8134
510-486-5988 (office)
https://hightech.lbl.gov/


Standardizing FWS connections, OCP ACS Immersion Solutions - Thread type, delta T

Don Mitchell <Don.Mitchell@...>
 

The Advanced Cooling – Facilities (ACF) subproject of OpenComputeProject requests your input on standardizing connections to OCP ACS Immersion solutions.

 

Thread connection standardization:   General feedback to date has been:

-          FWS connection point under 2” = metric thread (DN 25 or DN 40)

-          FWS connection point > 2” would grooved coupling connection (or possibly a flanged connection)

Is it better let every vendor choose their thread connection of preference and let the local pipefitter figure it out?

 

Input request:   Do you see benefit to OCP global standard of the connection to the tank options.  (with adaptors used per customer and regional preference)

 

Delta T range standardization: 

  • Diversity in Delta T expectations adds complexity to planning. 

Input Request:  Can the range of delta T options be reduced for OCP solutions.

 

Will be sending a similar survey to ACS Cold Plate and ACS RDHX teams

 

Attached below are workstreams we are seeking to finalize into WPs by end of summer. 

Would value insights on alignment with ACS Immersion guidance

 

 

 

Kind Regards

 

Don Mitchell

John Menoche, P.E.

 

Subproject Co-Leads for Advanced Cooling – Facilities

Progress reviewed

     Weekly OCP ACF calls Tuesdays 1100 ET (UTC-4)

     Weekly OCP Connection subcommittee calls Wednesdays 1100 ET (UTC -4)

     Monthly OCP ACF APAC update 3rd Wednesdays 0930 Singapore/Beiing time – UTC +8)

https://global.gotomeeting.com/join/952298085

 

 

Upcoming OCP Advanced Cooling Facilities Events

 

To be removed from future notices and invites, please respond with request to remove.

 

To get involved: 

1) Please become an OCP member and join the ACF Mailing List  :   https://ocp-all.groups.io/g/ocp-acf

2) Get familiar with the details on the Sub-Project on the ACF Wiki

3) Check our Project Calendar for more info. Call Info and agenda will be published via the mailing list reflector. 

 

To be removed from future notices and invites, please respond with request to remove.

 

 


Special OCP ACS Immersion call - Call for papers

Rolf Brink
 

https://global.gotomeeting.com/join/177040733

 

Please reserve this time for announcements and more details on the call for papers regarding OCP Global Summit - ACS Immersion.

 

Agenda:

Details and agenda to follow

 


Invitation: ACS - Immersion Cooling - Optional Extra Call to discuss ... @ Tue Jun 29, 2021 9am - 9:30am (CDT) (ocp-acs-immersion-cooling@ocp-all.groups.io)

Michael Schill
 

You have been invited to the following event.

ACS - Immersion Cooling - Optional Extra Call to discuss New Summit Guidelines

When
Tue Jun 29, 2021 9am – 9:30am Central Time - Chicago
Where
https://global.gotomeeting.com/join/177040733 (map)
Calendar
ocp-acs-immersion-cooling@ocp-all.groups.io
Who
Michael Schill - creator
paul.louvet@...
archna@...
daniele@...
davidm.online@...
dasartor@...
ocp-acs@ocp-all.groups.io
Daniel Pope
lkosch@...
rolf.brink@...
m.szadkowski@...
Caleb Lusk
margerisonrick@...
ocp-acs-immersion-cooling@ocp-all.groups.io
Steve MillsOCP
Antonia Tsoukatos
els.bronstring@...
This meeting is being recorded via audio and video. By participating you consent that this recording may be made publicly available. Any presentation materials, proposals and meeting minutes are published on the respective project's wiki page and is open to the public in accordance to OCP's Bylaws and IP Policy. This can be found at http://www.opencompute.org/participate/legal-documents/. If you have any questions please contact OCP. 

ACS - Immersion Cooling Sub-Project Call

Please join my meeting from your computer, tablet or smartphone.
https://global.gotomeeting.com/join/177040733

You can also dial in using your phone.
United States (Toll Free): 1 877 568 4106
United States: +1 (571) 317-3129

Access Code: 177-040-733

More phone numbers
Australia: +61 2 9087 3604
Austria: +43 7 2081 5427
Belgium: +32 28 93 7018
Brazil: +55 21 3500-3941
Canada: +1 (647) 497-9391
Denmark: +45 32 72 03 82
Finland: +358 923 17 0568
France: +33 170 950 594
Germany: +49 691 7489 928
Ireland: +353 16 572 651
Italy: +39 0 247 92 13 01
Mexico: +52 55 3687 7278
Netherlands: +31 207 941 377
New Zealand: +64 9 280 6302
Norway: +47 21 93 37 51
Spain: +34 932 75 2004
Sweden: +46 853 527 836
Switzerland: +41 225 4599 78
United Kingdom: +44 20 3713 5028

New to GoToMeeting? Get the app now and be ready when your first meeting starts:
https://global.gotomeeting.com/install/177040733

Going (ocp-acs-immersion-cooling@ocp-all.groups.io)?   Yes - Maybe - No    more options »

Invitation from Google Calendar

You are receiving this courtesy email at the account ocp-acs-immersion-cooling@ocp-all.groups.io because you are an attendee of this event.

To stop receiving future updates for this event, decline this event. Alternatively you can sign up for a Google account at https://calendar.google.com/calendar/ and control your notification settings for your entire calendar.

Forwarding this invitation could allow any recipient to send a response to the organizer and be added to the guest list, or invite others regardless of their own invitation status, or to modify your RSVP. Learn More.


Driving the focus group: Putting together an immersion cooling non-commercial "pitch deck"

Raúl Álvarez
 

Hi Rolf,

A kindly reminder to open the discussion.

Participation from the mailing list is welcome.

Best regards,

Raúl Álvarez
Lead Solution Architect
+34 637 950 957
Raúl's LinkedIn
Submer - Datacenters that make sense - https://submer.com
Follow Submer in:
     


Submer Technologies S.L. is a registered company with ID ESB66631375. Data ProtectionYou can enquire what information Submer stores about you and you can request access, rectification, limitation, opposition, portability or cancellation by sending an email to contact@.... Additional information can be found at https://submer.com/privacy-policyConfidentiality: This email and any attached files are intended for the named recipients only and may be confidential. If they have come to you in error, please notify the sender immediately. You should take no action based on them and should not copy or show them to anyone. 

1 - 20 of 87